C Touch
#1
Hi is it possible to have a alarm report on a c touch after the

alarm has been activated.eg(zone 4 @ 1205)

Many thanks,

Choppa.

Reply
#2
Yes, it is. The information on how to use C-Touch to show security status is described in the UCM/Cbus manual which can be downloaded from http:/www.cytech.biz
Select Product Infomration, Downloads/ Manuals in the left and look foro UCM/Cbus.
The section \"Linking Security Events on C-Bus\" has all the information that you need

Reply
#3
Hi.

 I am still having that issue with, reporting to c touch what zone set the

alarm off.All I am getting is a live status.

Is it possible that clipsal c touch can report what zone set the alarm off, even

hours after.


Thanks.
Reply
#4
I am afraid the ctouch does not have the facility to report historical status or event log, it only can show live status. However you may be able to program the Comfort zone Response to turn on a group address when in alarm, and in Cbus show the group address status on a special page This will show which zones caused the alarm
Quite a bit of programming but it may be a possible solution

Reply