I found that comfort can control lights w/ one 2-way switch.
In installed building, I have several 2-way switches and intermediate switch, ex.: on 1 group lamp, there are (2) 2-way switches & (1) intermediate switch, so totally (3) switches can control 1 group lamp in different location of wall but still in one room.
Also, mostly I have motion/presence detectors & Twilight sensors for control lights, with each sensor have a 1-way switch for back-up purpose.
And Rain sensor for control Louvre with 1-way series rockers switch (one for fully open/close louvre, another for adjust opening of louvre)
Since I\'d like to integrate all to comfort, please inform me a detail wiring diagram on those.
Thank you.
To control the same set of lights besides using the 2-way switch connected to the TWS01/02 module, you can easily connect other switches to the zones. By doing so, you would be using Comfort programming to control the lights by controlling the output connected to the TWS01/02 modules by simply toggling the output.
The motion sensors and light sensor would work in a similar manner, except that you would probably need to check the status of the light before deciding whether to switch on or off the light.
Posts: 18
Threads: 7
Joined: Aug 2006
Reputation:
0
So, for the 1[suP]st[/suP] 2way switch, I still need to connect to TWS01/02 module w/ 2x1.5mm wire & the 2[suP]nd [/suP]2way switch or intermediate switch only w/ data cat.5 cable?
Exactly, How many cable needed for each 2way switch?
Yes, that\'s right. You may not actually need to use actual 2 way switches for the 2nd case, normal 1-way switches will suffice. This is because you are just trying to find a way of triggering the zone ON and OFF responses. As such, all you will need is a pair of cable coming from each switch to the zone.
Posts: 18
Threads: 7
Joined: Aug 2006
Reputation:
0
Done w/ the 2-way switch.
In Movement sensor switch, there\'s not a 2-way system. Therefore, it can\'t use TWS01/02 module, right?
How many wire will be used to connect to comfort? so w/ touch panel, I can see the light status & trigger the sensor & light, even there\'s not any movement.
You can still use the TWS01/02 for the movement sensor. The movement sensor has its contacts connected to a zone, while another zone is used as feedback from the lighting circuit and the output used to control the TWS01/02\'s relays. This would allow the provision of connecting a 2-way switch to the circuit as a backup control.
Of course, alternatively, if there is no other method of controlling the light, other than depending purely on the movement sensor, a simpler method would be to have a suitable relay connected to an output. Then, you would have to monitor the output as the status. In this case, you would use 1 pair of wires for the connection between the relay and Comfort.
Posts: 18
Threads: 7
Joined: Aug 2006
Reputation:
0
Sorry, I don\'t quite understand about this sensor with TWS01/02 module. Furthermore, there is movement sensor w/ 2 outputs (one for light & another for fan), used in bathroom.
It would be great if you could attach a wiring diagram, since I have 30 movement sensors (10 w/ 2 outputs) & I\'d like to integrate all in Comfort without any mistakes.
Another thing, is there any problem encountered integrating exhaust fan switch such as interference to the main board or ...?
Regards.
Posts: 3,493
Threads: 476
Joined: Aug 2006
Reputation:
0
Slaves and RIOs are connected by the RS485 bus which can be several 100 meters from Comfort
Hence you can use these on the different floors and cnnect using a CAT 5 cable back to Comfort
LEM02-M2 which can connect to either a Comfort or Slave has 8 inputs and no outputs