I have a PSU02/230/3 expansion box which powers my cameras. The transformer has died (the primary has gone open circuit). So far as I can see from the documentation, the replacement transformer should have a secondary of 16 Volts at 5 Amps.
I have ordered a 15VACTX spare transformer from my supplier. The transformer I have received is rated 18 Volts at 20VA. My calculations suggest that this has only around a fifth of the power that I should have.
The supplied device is actually a CPC Transformer with the two 10VA secondary windings connected in parallel.
Am I missing something?
Thanks
I have ordered a 15VACTX spare transformer from my supplier. The transformer I have received is rated 18 Volts at 20VA. My calculations suggest that this has only around a fifth of the power that I should have.
The supplied device is actually a CPC Transformer with the two 10VA secondary windings connected in parallel.
Am I missing something?