New Project Requirement
#1
I have a new project requirement as per below :

1). Zone 12 - Use as keyswitch to Arm to Nightmode and to Disarm System (First time contact closed and opened Arms to Nightmode, the second time contacts closed and opened to Standy Mode or Disarm)

2). Zone 13 - Trigger alarm delay only when in Away Mode, When in Night Mode would trigger alarm instantly

3). When alarm is triggered, output 6 should be activated and after sign in output 6 is off.

4). Output programming from output 1 to 5 to control lighting. Eg : Output 1 is for Living Light, 2 for Dining Light and etc..

Hopefully the support team could provide me a sample programming with the above requirements in cclx format

Thank you.
Regards,
Joshua
Reply

#2

  1. See attached cclx file under Security >> Zones/Inputs >> Zone 12.
  2. For this I\'ve modified zone type MonitorNC (in Security Type Settings >> Zone Types) to work only in Away and Night Mode. Also set/clear a flag to keep track of what security mode Comfort system is currently in under Events >> Miscellaneous Events >> Away Mode and Night Mode Responses.
  3. This is programmed under Security Type Settings >> Alarm Types >> Intruder and Disarm alarm types to turn on/off output 6 accordingly.
  4. This is programmed under Control >> Control Menu >> Control Group 0 for Lights. This assumes Two Way Switch (TWS02) Modules are used to control the lights. The current sensors of TWS02 are fed-back to Zones/Inputs 1 to 5 to match the outputs 1 to 5 respectively.


Attached Files
.cclx   Joshua Project.cclx (Size: 216.69 KB / Downloads: 6)
Reply