I have a KNX Sensor (GA: 8/0/0) which I have mapped as a Virtual Input.
Sometimes this sensor triggers False Alarms, that I don\'t know how to explain why! (heat waves, maybe).
Is there a way to avoid these false alarms? Is this a known issue with KNX sensors?
Perhaps by programing something like: Only trigger alarm if it detects 3 times in 15 seconds. How can I do this with a Virtual Input?
Thank you.
Posts: 3,493
Threads: 476
Joined: Aug 2006
Reputation:
0
Hi Cristo
KNX sensors may be more prone to false alarms because their function is more for Presence Detection rather than alarms. Most KNX systems use them for switching on lights. Alarm sensors are designed to minimise false alarms (at least the good ones)
There is a Vibration Analyser Response 86 in the default cclx template which is shown below
If Timer Timer08 = 0 Then
Do NullResponse After 30 Seconds Using Timer08
Set Counter007 = 0
End If
Increment Counter007
If Counter Counter007 >= 3 Then
Stop Timer Timer08
Else
Skip Alarm
End If
This triggers alarm if there are 3 activations in 30 seconds, you can change the parameters
The Response should be assigned to the Virtual Input.
Alternatively you can use the Alert Zone Type. You need alert zones within 10 minutes to trigger an intruder alarm
Posts: 10
Threads: 1
Joined: Mar 2014
Reputation:
0
Thankyou for the reply.
I tried your sugestion but I think it\'s not working properly. When I arm the alarm, as soon as I apear to the sensor, it starts the entry time countdown (the knx sensor is an entry door). Even if I do a quick apear and hide.
I assigned the Vibration Analyzer to the On Response of the Zone. Is this right? I also tried the sensivity Zone Type 50 and then 850, but the behaviour was the same.
Am I doing something wrong?
Posts: 3,493
Threads: 476
Joined: Aug 2006
Reputation:
0
The response was not meant to work on an Entry Door zone. It is for an immediate zone that is active when armed
Try this instead
make the zone NOT entry door, but PIR Night/Away instead
Zone Response
If Timer Timer08 = 0 Then
Do NullResponse After 30 Seconds Using Timer08
Set Counter007 = 0
End If
Increment Counter007
If Counter Counter007 >= 3 Then
Stop Timer Timer08
Start entry Delay
Else
Skip Alarm
End If
I dont like having a PIR as an entry door. an entry door should be a real door so that it can be used as the final door arming for away mode.
Posts: 10
Threads: 1
Joined: Mar 2014
Reputation:
0
This KNX sensor is at entrance/exit. I will try later to see if it works.
How do I assign an entry Delay to a normal PIR at an entrance/exit where the keypad is installed? Entry Path?
Posts: 3,493
Threads: 476
Joined: Aug 2006
Reputation:
0
They are different things
Entry Path setting in a zone means the zone will not cause an alarm when there is movement after the entry door is opened for the duration of the entry delay
Entry Delay is the delay started by opening the Entry door when the system is armed. During entry delay the Entry path zones do not cause alarms
Posts: 10
Threads: 1
Joined: Mar 2014
Reputation:
0
Yes, that I understand. My question is:
How do I assign an entry Delay to a normal PIR (because you say one shouldn\'t assign Entry Door to a PIR) at an entrance/exit where the keypad is installed?
(there is no magnet on the fisical \"entry door\". There are only PIR\'s).
Posts: 3,493
Threads: 476
Joined: Aug 2006
Reputation:
0
\"Start entry delay\" assigned to a Pir zone will start an entry delay if it is not an entry doorThat becomes the same as making the Pir an entry door
What I meant is it is better to have a magnetic contact on a door rather than use a PIR as entry door
Posts: 10
Threads: 1
Joined: Mar 2014
Reputation:
0
Ok. So if there are only PIR\'s, the PIR that is nearest to the entry door should be configured as Entry Door, nevertheless, it is a better practice, to have a magnet sensor on the actual entry door, and have it configured as Entry Door. Is this it?