If the red D9 is blinking it means the UCM is replying, which also means that it received the correct message from Comfort, so the UCM must be communicating
Start the Bus monitor before the time that it happens. See what it captures when the fault happens
Posts: 6,025
Threads: 880
Joined: Apr 2006
Reputation:
3
The problem seems to be the RS485 bus (KA KB) has interference so that the messages are garbled
The NAK replies means that the checksum is wrong in the message
16: 52: 28: 056 ----< 03 53 4E 35 43 02 <--->SN5C NAK reply from/to Rio/Scs03
16: 52: 28: 072 ----< 03 53 4E 35 43 02 <--->SN5C NAK reply from/to Rio/Scs03
16: 52: 28: 185 ----< 03 12 4E 39 44 02 <--->N9D NAK reply from/to Ucm 02
16: 52: 28: 244 ----< 03 12 4E 39 44 02 <--->N9D NAK reply from/to Ucm 02
16: 52: 28: 306 ----< 03 12 4E 39 44 02 <--->N9D NAK reply from/to Ucm 02
16: 52: 28: 369 ----< 03 12 4E 39 44 02 <--->N9D NAK reply from/to Ucm 02
16: 52: 28: 533 ----< 03 51 4E 35 45 02 <--->QN5E NAK reply from/to Rio/Scs01
after this time, all the messages are NAKs
The switching on of the relay must be causing some sort of interference to the bus
Posts: 6,025
Threads: 880
Joined: Apr 2006
Reputation:
3
The intermittent NAKs started at 15:18 in the bus monitor, but became worse until 16:+ when it happens all the time
If you have an oscilloscope you can use it to see what the KA/KB signal looks like
Posts: 551
Threads: 64
Joined: Jan 2007
Reputation:
0
Hi Sychui,
No, dont have an oscilloscope unfortunately. I have been wathcin the NAKS over he last 20 mins, and counted 7 of them over that period. That was with the heating relay off.
Is the presence of NAK messages unusual or would you expect a number of them to come in even in a good system ?
Do you think that the vmb4ry is what is introducing the noise at this stage, and if so, how can it cross the velbus onto the comfort bus ?
Posts: 6,025
Threads: 880
Joined: Apr 2006
Reputation:
3
NAKs can occur occasionally on the Bus, which may be due to noise and interference.
Your problem seems to be interfence caused by the load switching on. It may or may not be due to Velbus.
Can you disconnect the load and turn it on manually eg using a switch so it is isolated from Velbus. Seee if that causes the same problem
Posts: 629
Threads: 62
Joined: Jan 2007
Reputation:
2
As a test, I ran my network for most of the night without even one NAK. That Keypad02 of yours looks a bit suspect...
Confirm that you receive NAKs for this device all the time or just when the boiler is On? If it\'s giving these errors all day then perhaps just remove this keypad for a while (as close to Comfort as possible to rule out induced noise in the KP02 cabling). I think in the absence of a clear culprit you need to try the process of elimination.