I have a working Fibaro Relay Module, so I know that the Comfort ZWave interface works ok.
I am trying to include my Fibaro Dimmer 2 (FGD-212) into my Comfort System. The sensor register reads the power figures from the bulbs, but there doesn\'t seem to be a way of controlling them - however they work fine from Vera.
Looking at the Comfort Manuals, I would have thought they would be sensed as a Multilevel Multichannel Switch but they are showing as a Multilevel Sensor. See attached screenshot. When I do a response to control them I am only given the choice of a Basic Get, a Basic Set and a Multichannel Get
Is this why I can read the power sensor but not control them and how would I fix this?
Hi, When I load a counter with a value the lights do not respond and stay off. I have tried 255, 99, 80 and other values. Strangely, after trying to set it with a counter the light then wont stay on with Vera - it just goes on for a moment then goes off again. If I manually use the switch everything settles down again but comfort cant control it.
12-02-2015, 12:53 AM (This post was last modified: 12-02-2015, 12:53 AM by LeeBurley.)
Its on 7.072 which is the latest I think.
If I set a counter on the Fibaro relay it works as expected, so it only the dimmers I am having major problems with.
Does the dimmer\'s counter value shows the value correctly, whenever dimmer state changes (eg. control the switch manually) ? Make sure that dimmer\'s counter is not used for other purposes elsewhere.
Other than upgrading UCM/Zwave to the latest version, it is best that Comfort Main is using the latest version too.
Also you can do a \"Learn\" operation again, so that the Z-Wave network recompute its route table. Take note that you do NOT need to \"Reset\" to default, before doing so.
Quote:Does the dimmer\'s counter value shows the value correctly, whenever dimmer state changes (eg. control the switch manually) ? Make sure that dimmer\'s counter is not used for other purposes elsewhere.
Other than upgrading UCM/Zwave to the latest version, it is best that Comfort Main is using the latest version too.
Also you can do a \"Learn\" operation again, so that the Z-Wave network recompute its route table. Take note that you do NOT need to \"Reset\" to default, before doing so.
Hi, Comfort and all its UCMs/RIO/KPs are at the latest firmware
When the switch is operated manually or through Vera the value in the counter is not updated, but the value of power usage is updated in the sensor
I have tried another learn and nothing has improved.
I unassigned the sensor so that only the counter remained. The light still doesn\'t work, and the on and off buttons also do not respond. I am sending you my cclx file on email. Thanks!
As you can see, the multilevel sensor command class transmission is in \"non secure\" method and basic command class is in \"secure\" method.
All this is consistent with what LeeBurley is experiencing.
Since UCM/Zwave does not support secure transmission, therefore Comfort sensor register gets updated while counter register does not. Also UCM/Zwave cannot control FGD-212 on/off and dimming.
In short, Fibaro Dimmer FGD-212 cannot work with our UCM/Zwave. This is because some command classes are transmitted in \"secure\" method, including the commonly used Basic command class.
FGD-212 will have difficulties working with many other controllers and devices, as most do not support secure transmission.