Problem with send message from c-bus to knx
#21
we can remove the restriction any any application address in Custom , as long as everyone using the product knows which applications will work similar to Lighting

I believe all aplications should accept the On/Off command. Other commands like dimming and Ramp may be handled diferently by other applicatioons
Reply
#22
I\'m sorry, but I\'m not quite understand your answers. 


I tested the new firmware and the main problem has been resolved, but I would like you to be taken into account the following points (please answer as soon as possible): 


1. Application â„–95 ($5F) in the c-bus network is reserved for the Dali protocol. I would like to have additional Application which is not reserved in C-bus Toolkit for any specialized tasks (besides the Application 48($30) which is already added). 
2. Application â„–136 ($ 88) – Heating is being used also in C-bus Toolkit software. It works the same way as an Application â„–56 ($38). Could you please also include the ability to retransmit Application â„–136 ($ 88)? 


In addition I have a question related to the C-bus system: Is there any support in any Applications of using the variables such as integer or float, which may pass through Your device in the KNX network? 
Thank you for your quick feedback.
Reply
#23
You can try cbusknx 1.007
You can add other cbus applications  which work like the lighgting application
Integer and Float are not suppoprted


Attached Files
.zip   cbusknx1_007.zip (Size: 15.49 KB / Downloads: 2)
Reply
#24
which applications you have done work in this firmware?
Reply
#25
There is no restriction on Custom applications as long as they work like the lighting application
Reply
#26
Problem with firmware V1_007.
Data from c-bus network Lighting Apl. 56 ($38) dont\'t transimt to knx network.
From knx to c-bus work ok.
test config in attachment. Test group 121


Attached Files
.zip   config_with_problem_v1_007.zip (Size: 1.61 KB / Downloads: 2)
Reply
#27
We cannot see the problem at all like you mentioned

In your file, you do not use Lighting application $38 (decimal 56) in Cbus to KNX
There are only applications 48 and 136 mapped to KNX scaling objects (1 byte)

what is working and what is not?
are you sending cbus applications 48 and 136 to KNX and do these work?

The version 1.007 simply allow any Cbus application number which is not 56 or Security application to be sent to KNX and behave just like a lighting application. It doe snot prveent lighting application from cbus to knx from working
Reply
#28


Attached Files Thumbnail(s)
   
Reply
#29
do you mean that ONLY application 56 does not work and the other custyom applications do work, or all applications are not working from cbus to knx?
Reply
#30
In this project i tested c-bus groups from Aplications 49, 56, 139.
Transfer c-bus groups from applications 49 and 139 works correctly in both directions.
Transfer c-bus groups from application 56 work only from KNX to C-Bus. C-bus Groups from Apl 56 dont transmit to KNX network. 
Reply