 Posted: Friday May 31st, 2013 12:35 pm
   
1st Post
slychiu
Administrator


Joined: Saturday Apr 29th, 2006
Location: Singapore
Posts: 5495
Status: 
Offline

  back to top

A UCM/ETHernet or UCM/USB is required for programming with Comfigurator. The UCM is required to program Comfort but is not required for normal operation, and can be removed after programming. However a UCM/ETH02 allows remote programming and access by iPad, iPhone, Android phone or tablet and is the recommended choice

The UCM used for programming by Comfigurator should have its ID set to 1. This is because UCM ID #1 can be removed from the system without causing a Communications Trouble alarm. UCMs from the factory are set to ID1 as default.
For instructions on how to set UCM ID, see http://www.comfortforums.com/forum4/3418.html

The UCM communications port must be selected
Go to Options > Settings as shown in the screenshot below. You must specify the connection method in order to connect Comfigurator to Comfort.

  • For Serial, select the COM port 1 to 64
  • For Network (Local) select the LAN IP Address and port
  • For Network (Internet) select the LAN IP Address and port. This may be a dynamic IP name eg comfort.dyndns.org  or a fixed IP address.
  • For USB select the serial number which appears in the serial number window
For instructions on setting the IP address and Port for the Network connections, go to the topic http://www.comfortforums.com/forum113/3402.html
See a video on Youtube on how to set up the ethernet connection https://www.youtube.com/watch?v=ctsr49Y-vZE

For instructions for using USB interface go to http://www.comfortforums.com/forum4/3404.html

Each of the 4 methods of connection, ie Serial, Network (Local), Network (Internet) and USB and the associated address is saved in the cclx file

This is very useful for Local and Internet IP connections as it saves you from having to remember and type the IP address and port when you connect from the local network or from the Internet.

The UCM Connection methods in Comfigurator are saved in the cclx file from Comfigurator 3.6.x


The connection setting can be seen in the Status bar at the bottom of the Comfigurator screen as shown below



Check that this connection method and address is correct before proceeding

To test the connection to Comfort, go to Transfer > System Information.
The log in window will appear as shown below. Enter the user code (default 1234) and press OK




If the connection setting is correct, the System Information screen should be displayed

Last edited on Sunday Jun 24th, 2018 05:46 am by slychiu



 Posted: Saturday Jun 1st, 2013 02:55 am
   
2nd Post
ident
Administrator


Joined: Wednesday Aug 9th, 2006
Location: Singapore
Posts: 3493
Status: 
Offline

  back to top

If the Connection settings are not correct, Comfigurator will not be able to connect to Comfort, and the following message will pop up



This does NOT mean the user code is wrong. It means the UCM Connection settings are incorrect.
The connection setting  is shown in the status bar


If the user code entered was wrong, the popup message  is shown below

Last edited on Saturday Jun 1st, 2013 06:23 am by ident



 Posted: Saturday Jun 1st, 2013 02:59 am
   
3rd Post
ident
Administrator


Joined: Wednesday Aug 9th, 2006
Location: Singapore
Posts: 3493
Status: 
Offline

  back to top

If the user code is wrong, the following message will pop up



Check that code entered is correct