Hi,
I have Comfort I Ultra (Action 4.227) with UCM/CUBS (Cbus 5.66).
Would I able to use Location 6420 to 6547 to monitor Counter 1 to 127. The documentation mentions (Outside version only)
Posts: 5,941
Threads: 868
Joined: Apr 2006
Reputation:
2
Note that the locations you mention are for Counter Responses.
For Ultra, the locations are not the same.
To find out what locations areused, startComfigurator 3, go to Events > Counters The locations are shown at the bottom left when you position the cursor on a Counter
eg for Counter 0
(4960) = 0,0
This means Location 4960, 2 bytes value of 0,0 as Ultra Responses are 2 byte values unlike Pro
Posts: 5,941
Threads: 868
Joined: Apr 2006
Reputation:
2
Yes you can have Counters 0 to 127 for Comfort I Ultra, as you can see them in Comfigurator when you select Comfort I Ultra