i had 5 TWS modules connected on lighting loads with consumption varied between 0.7Amp to 3 Amp, those current sensor of TWS can not sense any current and there is no sensitivity jumper there, so any suggestion for diagnosing or troubleshooting that issue.
thanks
Posts: 3,493
Threads: 476
Joined: Aug 2006
Reputation:
0
Did you try looping the wires through the TWS again to double the sensitivity?
Only 1 wire, ie the live wire should go through the current sensor not both live and neutral
How was the zone programmed, as Normally Open switch?
Do a Security Check F3,2 to anounce all zones that are on, including the TWS02 ones
If still have problems send a photo of the TWS02 connected
Posts: 56
Threads: 17
Joined: Aug 2008
Reputation:
0
thanks for useful help,
the situation now is:
7 Tws out of 10 was connected to slaves and LEM\'s and wasn\'t identify as Normal Open contact, it works after we changed the setting.
3 TWS out of 10 was connected to RIO, but did not work, we tried to double the turns even tripling it, but it didn\'t work as will ( sure only life wire go through).
it works when we connect external current with the normal senstivity without any turns duplication.
so any suggestion about those 3?
appreciated, thanks