TWS current sensor do not feedback
#1
i had 5 TWS modules connected on lighting loads with consumption varied between 0.7Amp  to 3 Amp, those current sensor of TWS can not sense any current and there is no sensitivity jumper there, so any suggestion for diagnosing or troubleshooting that issue.
thanks
Reply

#2
Did you try looping the wires through the TWS again to double the sensitivity?

Only 1 wire, ie the live wire should go through the current sensor not both live and neutral

How was the zone programmed, as Normally Open switch?

Do a Security Check F3,2 to anounce all zones that are on, including the TWS02 ones

If still have problems send a photo of the TWS02 connected
Reply

#3
thanks for useful help,
the situation now is:
7 Tws out of 10 was connected to slaves and LEM\'s and wasn\'t identify as Normal Open contact, it works after we changed the setting.
3 TWS out of 10 was connected to RIO, but did not work, we tried to double the turns even tripling it, but it didn\'t work as will ( sure only life wire go through).
it works when we connect external current with the normal senstivity without any turns duplication.
so any suggestion about those 3?
appreciated, thanks

Reply

#4
Quote:it works when we connect external current with the normal senstivity without any turns duplication.
I am not sure what the above sentence means. Is that referring to the 7 TWS connected to SEM/LEM?

Can you check the state of the RIO input when the current is on, eg

in Monitor I/O type I?51 where 51 hex is RIO ID 1 Input #1 (assuming RIO #1 Input 1 has TWSD connected to it)

The reply should be I?5101 if ON and I?5100 if OFF


I just want to check if the RIO Input is really reporting off or on




Reply