#11
Don\'t know why 161 is updating and not 129.






#12
Perhaps 161 is already on and not as a result of the Response
Please send your cclx file so we can see the firmware versions and test accordingly

#13
ident,

cclx file sent to suppoort

Brian

#14
We confirm a bug that RIO Outputs status are  updated when you check the Show Status box but subsequent changes do not update the RIO Outputs status correctly


  Output 129 updates Output 161 and so on

#15
Confirmed a bug found by BS85 that after the show status box is checked in Names > Outputs, the RIO outputs status updates the wrong output eg Output 129 updates output 161 and so on
This will be fixed in 3.5.2

#16
Important
A bug has been found in 3.5.x
Vocabulary Upgrade tends to fail at 0%
Please do NOT attempt to do Vocabulary upgrade with 3.5.0 or 3.5.1
Revert to 3.4.4 if you need to do Vocabulary upgrade

#17
The next (beta) version 3.5.2 will have the following changes

Bugs Fixed
  1. Bus Monitor and IR Learner were not able to use the UCM \"Saved Connection Settings\". They are now synchronised with whatever connection settings are used, saved or override.
  2. \"Show Status\"  for RIO updates status  updated the wrong RIO outputs in real time when Rio Outputs change
  3. Vocabulary Upgrade failed at 0%.
  4. In Z-Wave Configurator, Learn process did not terminate when an \"NA\" error reply is received. Had to cancel manually but learn has been completed successfully.
New Features
  1. Status Box for Events > RIO Inputs added
  2. Drag and drop Outputs and Inputs to a new number will not delete the target. Instead the source and target will be exchanged. eg you can drag Input 2 to Input 1. This exchanges Input 1 and 2 numbers, and all responses and events which reference the inputs will now be changed to the new numbers. This is very useful if input and output numbers need to be changed due to mistakes and other constraints (or mistakes)
Improvements

  1. Fixed a problem of file system conversion causing exception
Known Issues
  1. Read from Comfort may change some Responses from eg KNX to Cbus (this is a pre-existing problem)
  2. In Universal UCM Configurator, the items in Comfort -> Device do not prevent more than 150 lines which is the maximum, but it will fail to write to EEPROM
  3. Vocabulary Upgrade VP command times out at 36 seconds which is still too shorty as some systems need more than that
  4. In Modules Tab, Add Keypad = KT03 does not show KT03 Confdigurator. Only Scan for KT03 allows the KT03 Configurator to be seen
  5. For KNX Configurator, KNX to Comfort,  Drive Control 1-bit message is not written to KNX EEPROM. This causes a Bug in UCM/KNX to occur, that a received group address on the Drive Control group address may cause a Spurious Response in Comfort to be activated