I have a number of items controlled by Cbus, and also some by Comfort. The two communicate via the CBus UCM. Is it possible for the CBus to transmit an ASCII code to comfort in order to bypass zones as it makes things operate? If so, does anybody know how? There is no mention I can see in either PICED or toolkit manuals.
TIA
Posts: 113
Threads: 14
Joined: Aug 2006
Reputation:
0
Hi Julian
I have achieved this by connecting a straight UCM to a Rs232 output of a Cbus colour touch screen, a PAC would work as well.
The first thing you have to send is the Comfort log-on code from Cbus
I can\'t be much more help as I never turned into a working system.
I had it set up for Homevision to talk to Comfort so substituting Homevision with Cbus was easy to test.
It is easy to test the asci code you want to send to Comfort as you can cut and past them into the UCM I/O Monitor in Comfigurator.
As far a I am aware the cbusUCM will only allow Cbus to change counter values in its present form.
Hope this helps
Mike
Posts: 3,493
Threads: 476
Joined: Aug 2006
Reputation:
0
I dont think cbus is able to send ASCII text but you can use a group address mapped to a counter Response to bypass zones
Posts: 629
Threads: 62
Joined: Jan 2007
Reputation:
2
Look into PAC/CTouch Logic, there are commands to send ASCII strings out the serial port. I\'ve never done it myself but a few guys on the Cbus forum connected various RS232 devices EG. weather stations etc. to a PAC or CTouch.
Ingo
Thank you all very much. I can see the way forward now.