06-15-2026, 03:52 PM
(06-14-2026, 04:37 PM)cc_uk Wrote: This weekend I swapped the CM9000 for the CM9001/A
Everything has gone well, but a few observations and questions
The CM9001/A is running Firmware 8.034. It's inbuilt UCM running 8.023
The system has the ETH03 module directly installed on the CM9001/A board.
There is a LEM connected via the ribbon cable, and a SEM running 7.207
I have two keypads - both KP01A running 7.016
Finally an 8 button SCS version 2.004
My first question - does the in-built UCM get updated with the main controller firmware or separately?
My main issue is around the 8 button SCS. Initially is scanned OK but then I started to see communications failure and it would appear with random IDs when scanning.
Jumpers ABCD all had a link set on them which should indicate Id 1.
I removed all jumpers cleaned the contacts, which looks good anyway, and got the same result. I used a meter to confirm that continuity was set on all 4 jumper pairs - and again all checks out OK.
By deleting the SCS and then re-scanning it has appeared again with Id 1. However when I press any of the buttons on the SCS - Comfort does not respond with the response I have set for them, and the LED just flashes continually after that. in SCS/RIO responses I have set it to monitor, and all of the ModuleStatus for 129-136 always stays set to Off
I am also using the SCS temperature monitor the value from this does appear to be being read into Sensor08
Any ideas? I know the SCS is old, but hoping it is still compatible with the ARM edition of the controller, especially as there is nothing to replace it.
Lastly since I have the latest controller now - should it return it's serial number when scanned? As mine doesn't.
You dont say what version of comfig you are using - in my last recent post I have suggested that Comfig 4 should only be used on totally new installations.