Action 102 - Alarm Zone
#1
Hi there,

I have two rooms I want to have a monitoring alarm call on when the system is disarmed - i.e. receive a call if someone unlocks and goes into the rooms when the system is in Security Off - I have therefore set a conditional action \'on response\' using Action 102 (as in Away mode I want the sensors to function as normal security sensors).

I am using a Familycare Alarm using Action 102, which works except the Zone doesn\'t announce in the alarm call, which means I don\'t know which of the two spaces have been entered.

Anyone know what am I doing wrong?

Henley
Reply

#2
Action 102 reports the last zone in alarm so it may not give the zone you need

I suggest to use another unused alarm type for the other znes ie 2 alarm types for 2 zones you want to report so that each alarm type is for one zone report only
Reply

#3
Thanks ident, I\'ll try that.

Neither zone is in \'alarm\', as such because the system is disarmed and the sensors remain part of the alarm system - i.e. zone alert type.

I am using action 102 in an On Response with a conditional if security mode = \'security off\'.

Henley
Reply

#4
Bear in mind that you wont get this to work on a C1 board - your other post as well NEEDS a C2 board upgraded to the latest firmware.
Reply