CBUS activation on reset - phantom activation
#1
I had reported this in the CBUS forums as a couple of external lights are being turned on by something - we didnt know what.

Now, I\'ve done some config changes today and I\'ve noticed that after a full download to comfort, when it resets \"says security off\" CBUS ids 34 and 36 are turned on (both lights on relay channels)

Where should I be looking for what is causing this ? The \"startup\" response is NULL...is it Comfort ? Is it CBUS ? Is it the CBUSUCM ?

 

 
Reply

#2
found it i think

 

I have a dodgy outside magnetic door sensor for the side gates  and it;s permantently open. i think comfort must be activating the automatic lights sequence as soon as it reboots...

 

 
Reply

#3
Remember that any active zone at reset will activate its ON response, as all zones are assumed to be OFF at reset

Reply