Hi, Since I upgraded my firmware for my GSM2 board a few weeks ago I am having an intermitting problem. Sometimes the green power light flashes on the keypad. When you type in your code it says SMS TROUBLE RESTORED. You can reset or arm the system and everything is OK. Other times when you turn the alarm off maybe after a few hours or minutes (sometimes it may not happen for a few days) a beeping comes from the keypad, on the keypad it says UCM2. I had powered this from the ETH02 board with the white cable and changed it to the KA, KB etc. but still the same. ttached is a copy of the event log from the system foe today. Any ideas!!!!
This is a false indication which has been identified
To turn off this alert, please go to Security Types > Nondetector alarms, set Nondetector Alarm 22 to Null alarm
Please check out the topic at http://www.comfortforums.com/forum48/2433.html
Should i change this entry then Chiu?
I\'m getting the flashing green light!!
Sorry for the questions but i cant see where the DailFailure came from!
Mike
Hi Chiu
I think I see what is happening
Are my names set from my original comfort install years ago?
Should I change these all back to the new names?
Mike
There is no need to change any names, as they are just descriptions
Alarm 22\"Dial Failure\" is the cause of the SMS Trouble intermittent that you have been getting. This is not a real alarm but due to network fluctuations
To get rid of it just set the assigned alarm type currently \"ARCCommsFail\" to the null alarm (blank)
This should not have been caused by Comfigurator 3.3.3, as that should not affect the alarm type settings unless you start a new default cclx file