05-29-2012, 06:43 PM (This post was last modified: 05-29-2012, 06:45 PM by ruirego.)
ok, I\'ll try tomorrow with a LEM01.
So, the procedure is to change the programmed outputs (op1, op2...) to the outputs of the LEM (op9, op10..) and see if they actuate, right?
I have a picture of the panel, can you confirm that the OP01 submodule is the signaled in the picture? If i\'m not using outputs in a panel can I remove it?
No. What you have is the old Comfort 1, not Comfort 2
Comfort 1 does not have the Op1 submodule as you can see from the photo. OP1 is a small board not an IC
You have pointed the arrow to the U5 IC which does drive the outputs on Comfort i
You can remove the U5 IC from SEM or Comfort and plug it into the other module to check if the prioblem is due to the U5 damaged
Be careful to switch off the power and remove battery before doing so
The U5 IC can be removed permanently if the module outputs are not used
I had a similar issue with my main panel, Output 1 remained off permanently, while 2-8 were always on. I had an old SEM which I replaced a few days before, so decided to take the OP1 submodule from there. The main board stopped working (similar to what the SEM was replaced for), which suggest that the issue might have been the OP1 submodule on the SEM to start with.
In any case I then tested with the OP1 submodule from the new SEM, and all the ports worked. So I need to order the submodule or two.
While on the subject of outputs, Configurator (3.7.6.0)shows Output00 as the first output, any reason for this?
The OP01 output was designed to be pluggable because it is easy to damage outputs, depending on what is connnected to them
If an output is in the ON state, any surge on the output wiring can cause the output to be damaged. This is why if an output is connected to a relay, the relay should be near to the output and not connected by a cable running a long distance
Output 00 in the Output action means the Output number is not fixed but is taken from the result of the previous action
eg
get Counter 1
Set Output 00
If counter 1 value is 5, then the next action sets output 5